Question:

What will happen if an electric oven of rating 3 kW; 220 V is operated in a domestic electric circuit (220 V) that has a current rating of 10 A? Give reason to justify your answer.

Show Hint

Always check the appliance’s current requirement to avoid overloading the circuit.
Hide Solution
collegedunia
Verified By Collegedunia

Solution and Explanation

The fuse of the circuit will blow and the circuit will break.
First, calculate the current drawn by the oven: \[ P = VI \quad \Longrightarrow \quad I = \frac{P}{V} \] Given: $P = 3000$ W,\; $V = 220$ V \[ I = \frac{3000}{220} \approx 13.64 \text{ A} \] So, the oven will draw about 13.6 A, which is higher than the circuit’s current rating of 10 A. The fuse wire in the circuit is designed to melt when the current exceeds 10 A to protect the circuit from overheating or fire hazards. Therefore, the fuse will blow and the circuit will open.