Question:

A simple vapor compression refrigeration cycle with ammonia as the working fluid operates between 30°C and -10 °C as shown in the following figure. The saturated liquid and vapor enthalpies at 30 °C and -10 °C are provided in the table below. If the COP of the cycle is 5.6, the specific enthalpy at the inlet to the condenser is .................... kJ/kg (round off to the nearest integer) 

Show Hint

For cycle problems, always start by sketching the diagram (if not given) and labeling the states. Use the property tables to find enthalpies at saturated liquid and vapor points. Remember that throttling is an isenthalpic process (\(h=const\)) and ideal compression is isentropic (\(s=const\)).
Updated On: Aug 30, 2025
Hide Solution
collegedunia
Verified By Collegedunia

Solution and Explanation

Step 1: Understanding the Concept:
The problem asks for the enthalpy at the compressor outlet (inlet to the condenser), given the cycle's Coefficient of Performance (COP) and state properties. We need to analyze the standard vapor compression refrigeration cycle and use the definition of COP.
Step 2: Key Formula or Approach:
The COP of a refrigerator is the ratio of the desired effect (heat absorbed from the cold space, or refrigerating effect \(Q_e\)) to the required input (compressor work \(W_{in}\)). \[ COP = \frac{Q_e}{W_{in}} \] Using the state points from the provided diagram:
- Refrigerating Effect (evaporator): \(Q_e = h_2 - h_1\)
- Compressor Work: \(W_{in} = h_3 - h_2\)
We need to find \(h_3\).
Step 3: Detailed Explanation or Calculation:
From the diagram and the problem description:
- The evaporator operates at -10 °C. State 2 is the outlet of the evaporator, so it is saturated vapor at -10 °C.
- The condenser operates at 30 °C. State 4 is the outlet of the condenser, so it is saturated liquid at 30 °C
- Process 4 -> 1 is the throttling process, which is isenthalpic (\(h_4 = h_1\)).
- Process 2 -> 3 is the compression process. Point 3 is the inlet to the condenser.
1. Determine enthalpies at key points from the table:
- Enthalpy at evaporator outlet (state 2, sat. vapor at -10°C): \(h_2 = h_g(-10°C) = 1420\) kJ/kg.
- Enthalpy at condenser outlet (state 4, sat. liquid at 30°C): \(h_4 = h_f(30°C) = 320\) kJ/kg.
2. Determine enthalpy at evaporator inlet (state 1):
Since 4 -> 1 is throttling, \(h_1 = h_4 = 320\) kJ/kg.
3. Calculate the Refrigerating Effect (\(Q_e\)): \[ Q_e = h_2 - h_1 = 1420 - 320 = 1100 \text{ kJ/kg} \] 4. Calculate the Compressor Work (\(W_{in}\)) using the COP: \[ W_{in} = \frac{Q_e}{COP} = \frac{1100}{5.6} \approx 196.428 \text{ kJ/kg} \] 5. Calculate the enthalpy at the condenser inlet (state 3):
The compressor work is the change in enthalpy across the compressor. \[ W_{in} = h_3 - h_2 \implies h_3 = h_2 + W_{in} \] \[ h_3 = 1420 + 196.428 = 1616.428 \text{ kJ/kg} \] Step 4: Final Answer:
Rounding to the nearest integer, the specific enthalpy at the inlet to the condenser is 1616 kJ/kg.
Step 5: Why This is Correct:
The solution follows the standard analysis of a vapor compression cycle. By identifying the states from the diagram and table, we can calculate the refrigerating effect. Using the given COP, we then find the work input, which allows us to determine the enthalpy at the compressor outlet, \(h_3\). The result of 1616 kJ/kg matches the provided answer range.