In the circuit shown, \( Z_1 = 50 \angle -90^\circ \, \Omega \) and \( Z_2 = 200 \angle -30^\circ \, \Omega \). It is supplied by a three-phase 400 V source with the phase sequence being R-Y-B. Assume the wattmeters \( W_1 \) and \( W_2 \) to be ideal. The magnitude of the difference between the readings of \( W_1 \) and \( W_2 \) in watts is _______________ (rounded off to 2 decimal places).
Step 1: Apply the two-wattmeter method
The two-wattmeter method is used to measure power in a three-phase system.
Given line voltages:
\[ V_{RY} = 400 \angle 0^\circ,\quad V_{YB} = 400 \angle -120^\circ,\quad V_{BR} = 400 \angle -240^\circ \]
The phase sequence is \( R \rightarrow Y \rightarrow B \).
Step 2: Calculate line currents
From the circuit:
\[ I_1 = \frac{V_{RY}}{Z_1} = \frac{400 \angle -60^\circ}{50 \angle -90^\circ} = 8 \angle 30^\circ \text{ A} \]
\[ I_2 = \frac{V_{RY}}{Z_2} = \frac{400 \angle 0^\circ}{200 \angle -30^\circ} = 2 \angle 30^\circ \text{ A} \]
Total line current:
\[ I_L = I_1 + I_2 = 10 \angle 30^\circ \text{ A} \]
Step 3: Calculate wattmeter readings
Wattmeter \(W_1\):
\[ W_1 = V_{RY} I_L \cos(\angle V_{RY} - \angle I_L) \]
\[ W_1 = 400 \times 10 \times \cos(-60^\circ - 30^\circ) \]
\[ W_1 = 4000 \cos(90^\circ) = 0 \text{ W} \]
Wattmeter \(W_2\):
\[ W_2 = V_{YB} I_2 \cos(\angle V_{YB} - \angle I_2) \]
\[ W_2 = 400 \times 2 \times \cos(-120^\circ - 30^\circ) \]
\[ W_2 = 800 \cos(-150^\circ) \]
\[ W_2 = -800 \cos(30^\circ) = -800 \times \frac{\sqrt{3}}{2} = -692.82 \text{ W} \]
Step 4: Difference between wattmeter readings
\[ |W_1 - W_2| = |0 - (-692.82)| = 692.82 \text{ W} \]
Final Answer:
|W_1 - W_2| \approx 693 \text{ W}
A continuous time periodic signal \( x(t) \) is given by: \[ x(t) = 1 + 2\cos(2\pi t) + 2\cos(4\pi t) + 2\cos(6\pi t) \] If \( T \) is the period of \( x(t) \), then evaluate: \[ \frac{1}{T} \int_0^T |x(t)|^2 \, dt \quad {(round off to the nearest integer).} \]
The maximum percentage error in the equivalent resistance of two parallel connected resistors of 100 \( \Omega \) and 900 \( \Omega \), with each having a maximum 5% error, is: \[ {(round off to nearest integer value).} \]
Consider a distribution feeder, with \( R/X \) ratio of 5. At the receiving end, a 350 kVA load is connected. The maximum voltage drop will occur from the sending end to the receiving end, when the power factor of the load is: \[ {(round off to three decimal places).} \]
In the circuit with ideal devices, the power MOSFET is operated with a duty cycle of 0.4 in a switching cycle with \( I = 10 \, {A} \) and \( V = 15 \, {V} \). The power delivered by the current source, in W, is: \[ {(round off to the nearest integer).} \] 
The induced emf in a 3.3 kV, 4-pole, 3-phase star-connected synchronous motor is considered to be equal and in phase with the terminal voltage under no-load condition. On application of a mechanical load, the induced emf phasor is deflected by an angle of \( 2^\circ \) mechanical with respect to the terminal voltage phasor. If the synchronous reactance is \( 2 \, \Omega \), and stator resistance is negligible, then the motor armature current magnitude, in amperes, during loaded condition is closest to: \[ {(round off to two decimal places).} \]