The incremental cost curves of two generators (\( \text{Gen A} \) and \( \text{Gen B} \)) in a plant supplying a common load are shown. If the incremental cost of supplying the common load is \( \lambda = 7400 \, \text{Rs/MWh} \), the common load in MW is ________________ (rounded to the nearest integer).
Given:
\( \lambda = 7400 \; \text{Rs/MWh} \)
Incremental cost equations:
For generator A:
\( I_{CA}(P_{GA}) = \dfrac{2000}{100} P_{GA} + 8000 = 20P_{GA} + 8000 \)
For generator B:
\( I_{CB}(P_{GB}) = 40P_{GB} + 6000 \)
Apply equal incremental cost criterion
\( \lambda = I_{CA} = I_{CB} = 7400 \)
For generator A:
\( 20P_{GA} + 8000 = 7400 \)
\( P_{GA} = -30 \;\text{MW} \)
Since generation cannot be negative:
\( P_{GA} = 0 \)
For generator B:
\( 40P_{GB} + 6000 = 7400 \)
\( P_{GB} = \dfrac{7400 - 6000}{40} = 35 \;\text{MW} \)
Total load supplied:
\( P_{GA} + P_{GB} = 0 + 35 = \mathbf{35 \; MW} \)
Final Answer:
The common load is 35 MW.
In the figure shown, self-impedances of the two transmission lines are 1.5j p.u each, and $Z_m = 0.5j$ p.u is the mutual impedance. Bus voltages shown in the figure are in p.u. Given that $\delta > 0$, the maximum steady-state real power that can be transferred in p.u from Bus-1 to Bus-2 is

A continuous time periodic signal \( x(t) \) is given by: \[ x(t) = 1 + 2\cos(2\pi t) + 2\cos(4\pi t) + 2\cos(6\pi t) \] If \( T \) is the period of \( x(t) \), then evaluate: \[ \frac{1}{T} \int_0^T |x(t)|^2 \, dt \quad {(round off to the nearest integer).} \]
The maximum percentage error in the equivalent resistance of two parallel connected resistors of 100 \( \Omega \) and 900 \( \Omega \), with each having a maximum 5% error, is: \[ {(round off to nearest integer value).} \]
Consider a distribution feeder, with \( R/X \) ratio of 5. At the receiving end, a 350 kVA load is connected. The maximum voltage drop will occur from the sending end to the receiving end, when the power factor of the load is: \[ {(round off to three decimal places).} \]
In the circuit with ideal devices, the power MOSFET is operated with a duty cycle of 0.4 in a switching cycle with \( I = 10 \, {A} \) and \( V = 15 \, {V} \). The power delivered by the current source, in W, is: \[ {(round off to the nearest integer).} \] 
The induced emf in a 3.3 kV, 4-pole, 3-phase star-connected synchronous motor is considered to be equal and in phase with the terminal voltage under no-load condition. On application of a mechanical load, the induced emf phasor is deflected by an angle of \( 2^\circ \) mechanical with respect to the terminal voltage phasor. If the synchronous reactance is \( 2 \, \Omega \), and stator resistance is negligible, then the motor armature current magnitude, in amperes, during loaded condition is closest to: \[ {(round off to two decimal places).} \]