Step 1: Recall economic dispatch principle.
For economic load dispatch without transmission losses, the incremental cost (marginal cost) of both units must be equal:
\[
\frac{dF_{1}}{dP_{G1}} = \frac{dF_{2}}{dP_{G2}} = \lambda
\]
Step 2: Compute incremental costs.
\[
\frac{dF_{1}}{dP_{G1}} = 0.2aP_{G1} + 40
\]
\[
\frac{dF_{2}}{dP_{G2}} = 0.4P_{G2} + 30
\]
At initial $a$ and dispatch values $P_{G1} = 175, P_{G2} = 115$:
\[
\lambda = 0.2a(175) + 40 = 35a + 40
\]
\[
\lambda = 0.4(115) + 30 = 46 + 30 = 76
\]
So,
\[
35a + 40 = 76 \Rightarrow 35a = 36 \Rightarrow a \approx 1.0286
\]
Step 3: Effect of increasing $a$ by 10%.
New $a' = 1.0286 \times 1.1 \approx 1.1314$
Now, the marginal cost of generator 1 increases faster with $P_{G1}$ because the coefficient $0.2a$ has increased. To restore equality of incremental costs:
- $P_{G1}$ must decrease (so that $\frac{dF_{1}}{dP_{G1}}$ reduces).
- Correspondingly, $P_{G2}$ must increase to keep the total load constant at $290 \, MW$.
Step 4: Effect on total cost $F$.
Since the unit 1 cost curve has become "steeper" (more expensive per MW), and more generation shifts to unit 2, the overall total cost $F$ will increase.
Step 5: Final outcome.
\[
P_{G1} \; \text{decreases}, F \; \text{increases}.
\]
% Final Answer
\[
\boxed{\text{Option (A): $P_{G1}$ decreases and $F$ increases.}}
\]
Two generators have cost functions with incremental-cost characteristics:
\[ \frac{dF_1}{dP_1} = 40 + 0.2 P_1, \frac{dF_2}{dP_2} = 32 + 0.4 P_2 \] They must supply a total load of 260 MW. Find the optimal generation (economic dispatch) ignoring losses.
A continuous time periodic signal \( x(t) \) is given by: \[ x(t) = 1 + 2\cos(2\pi t) + 2\cos(4\pi t) + 2\cos(6\pi t) \] If \( T \) is the period of \( x(t) \), then evaluate: \[ \frac{1}{T} \int_0^T |x(t)|^2 \, dt \quad {(round off to the nearest integer).} \]
The maximum percentage error in the equivalent resistance of two parallel connected resistors of 100 \( \Omega \) and 900 \( \Omega \), with each having a maximum 5% error, is: \[ {(round off to nearest integer value).} \]
Consider a distribution feeder, with \( R/X \) ratio of 5. At the receiving end, a 350 kVA load is connected. The maximum voltage drop will occur from the sending end to the receiving end, when the power factor of the load is: \[ {(round off to three decimal places).} \]
In the circuit with ideal devices, the power MOSFET is operated with a duty cycle of 0.4 in a switching cycle with \( I = 10 \, {A} \) and \( V = 15 \, {V} \). The power delivered by the current source, in W, is: \[ {(round off to the nearest integer).} \] 
The induced emf in a 3.3 kV, 4-pole, 3-phase star-connected synchronous motor is considered to be equal and in phase with the terminal voltage under no-load condition. On application of a mechanical load, the induced emf phasor is deflected by an angle of \( 2^\circ \) mechanical with respect to the terminal voltage phasor. If the synchronous reactance is \( 2 \, \Omega \), and stator resistance is negligible, then the motor armature current magnitude, in amperes, during loaded condition is closest to: \[ {(round off to two decimal places).} \]