Step 1: Recall $Y_{\text{bus}$ properties.}
- Off-diagonal entry $Y_{ij}$ corresponds to $-Y_{line}(i,j)$.
- Diagonal entry $Y_{ii}$ is the sum of admittances connected to bus $i$, i.e.
\[
Y_{ii} = \sum_{j\neq i} Y_{line}(i,j) + Y_{\text{shunt},i}.
\]
Step 2: Check line admittances from off-diagonal terms.
From the matrix:
- Between bus 1 and bus 2: $Y_{12} = j10 \;\Rightarrow\; Y_{line}(1,2)= -j10$.
- Between bus 1 and bus 3: $Y_{13} = j5 \;\Rightarrow\; Y_{line}(1,3)=-j5$.
- Between bus 2 and bus 3: $Y_{23} = j4 \;\Rightarrow\; Y_{line}(2,3)=-j4$.
Thus, three lines exist: 1–2, 1–3, 2–3.
Step 3: Check diagonal entries.
- For bus 1:
\[
Y_{11} = -j15, \text{expected from lines } = -(j10+j5) = -j15.
\]
So no shunt element at bus 1.
- For bus 2:
\[
Y_{22} = -j13.5, \text{expected from lines } = -(j10+j4) = -j14.
\]
Difference: $0.5j$, indicating a shunt capacitor at bus 2.
- For bus 3:
\[
Y_{33} = -j8, \text{expected from lines } = -(j5+j4) = -j9.
\]
Difference: $j1$, indicating a shunt capacitor at bus 3.
Step 4: Interpret results.
- All three lines (1–2, 1–3, 2–3) have line charging capacitances.
- Shunt capacitances are present at bus 2 and bus 3.
Step 5: Evaluate options.
- (A) True: All three lines have finite capacitances.
- (B) False: Not only line 2–3, all lines exist. This can NOT be true.
- (C) False: Shunt capacitor is not at bus 1, but at buses 2 and 3.
- (D) False: Shunt capacitor is not only at bus 3, but also at bus 2.
% Final Answer
\[
\boxed{\text{Option (B)}}
\]
A continuous time periodic signal \( x(t) \) is given by: \[ x(t) = 1 + 2\cos(2\pi t) + 2\cos(4\pi t) + 2\cos(6\pi t) \] If \( T \) is the period of \( x(t) \), then evaluate: \[ \frac{1}{T} \int_0^T |x(t)|^2 \, dt \quad {(round off to the nearest integer).} \]
The maximum percentage error in the equivalent resistance of two parallel connected resistors of 100 \( \Omega \) and 900 \( \Omega \), with each having a maximum 5% error, is: \[ {(round off to nearest integer value).} \]
Consider a distribution feeder, with \( R/X \) ratio of 5. At the receiving end, a 350 kVA load is connected. The maximum voltage drop will occur from the sending end to the receiving end, when the power factor of the load is: \[ {(round off to three decimal places).} \]
In the circuit with ideal devices, the power MOSFET is operated with a duty cycle of 0.4 in a switching cycle with \( I = 10 \, {A} \) and \( V = 15 \, {V} \). The power delivered by the current source, in W, is: \[ {(round off to the nearest integer).} \] 
The induced emf in a 3.3 kV, 4-pole, 3-phase star-connected synchronous motor is considered to be equal and in phase with the terminal voltage under no-load condition. On application of a mechanical load, the induced emf phasor is deflected by an angle of \( 2^\circ \) mechanical with respect to the terminal voltage phasor. If the synchronous reactance is \( 2 \, \Omega \), and stator resistance is negligible, then the motor armature current magnitude, in amperes, during loaded condition is closest to: \[ {(round off to two decimal places).} \]