Step 1: System description.
The network has three buses: Bus 1 (generator source), Bus 2 (junction), and Bus 3 (feeding an $R$--$L$ load).
- Line 1 connects Bus 1 to Bus 2 through breakers $B_{1}$ and $B_{3}$ with relays $R_{1}$ and $R_{3}$.
- Line 2 connects Bus 1 to Bus 2 through breakers $B_{2}$ and $B_{4}$ with relays $R_{2}$ and $R_{4}$.
- Line 3 connects Bus 2 to Bus 3 through breakers $B_{5}$ and $B_{7}$ with relays $R_{5}$ and $R_{7}$.
- Loads are connected at Bus 2 (via $B_{6}$ and $R_{6}$) and at Bus 3 (via $B_{8}$ and $R_{8}$). The source breaker is $B_{9}$ with relay $R_{9}$.
Step 2: Condition for selective protection.
The objective is to isolate only the faulty section with minimum disturbance to the healthy system. Overcurrent (OC) relays can detect excessive current, but when there are multiple sources or parallel paths, OC relays alone cannot distinguish the fault direction. In such cases, directional overcurrent relays (DOCRs) are required.
Step 3: Where are directional relays needed?
- For faults on Line 1: Current can flow from Bus 1 to Bus 2 or from Bus 2 to Bus 1 (depending on fault location). To avoid tripping from the wrong side, $R_{3}$ must be directional (blocking reverse current into Bus 2).
- For faults on Line 2: Similar reasoning applies, so $R_{4}$ must also be directional.
- For faults on Line 3: Only one source (Bus 1 via Bus 2) supplies Bus 3, so current direction is unidirectional. Thus, simple overcurrent relays $R_{5}$ and $R_{7}$ are sufficient; no directional relay is required.
- For loads at Bus 2 and Bus 3: The fault current always comes from Bus 1; hence simple overcurrent relays ($R_{6}$, $R_{8}$) are adequate.
Step 4: Minimum number of directional relays.
To achieve selectivity with minimum directional relays:
- Only $R_{3}$ and $R_{4}$ need to be directional (to discriminate between through-faults and actual line faults).
- Adding more directional relays (such as $R_{5}$ or $R_{7}$) is unnecessary and would not reduce the isolated portion.
Step 5: Verify the options.
- Option (A): Incomplete, because it specifies blocking towards Bus 2 but not line-specific direction.
- Option (B): Requires an extra directional relay $R_{7}$, which is unnecessary.
- Option (C): Uses four directional relays, which violates the minimum requirement condition.
- Option (D): Correct, since only $R_{3}$ and $R_{4}$ (on Bus 2 ends of Line 1 and Line 2) must be directional.
% Final Answer
\[
\boxed{\text{The correct option is (D): $R_{3}$ and $R_{4}$ as directional relays on Line 1 and Line 2.}}
\]
A continuous time periodic signal \( x(t) \) is given by: \[ x(t) = 1 + 2\cos(2\pi t) + 2\cos(4\pi t) + 2\cos(6\pi t) \] If \( T \) is the period of \( x(t) \), then evaluate: \[ \frac{1}{T} \int_0^T |x(t)|^2 \, dt \quad {(round off to the nearest integer).} \]
The maximum percentage error in the equivalent resistance of two parallel connected resistors of 100 \( \Omega \) and 900 \( \Omega \), with each having a maximum 5% error, is: \[ {(round off to nearest integer value).} \]
Consider a distribution feeder, with \( R/X \) ratio of 5. At the receiving end, a 350 kVA load is connected. The maximum voltage drop will occur from the sending end to the receiving end, when the power factor of the load is: \[ {(round off to three decimal places).} \]
In the circuit with ideal devices, the power MOSFET is operated with a duty cycle of 0.4 in a switching cycle with \( I = 10 \, {A} \) and \( V = 15 \, {V} \). The power delivered by the current source, in W, is: \[ {(round off to the nearest integer).} \] 
The induced emf in a 3.3 kV, 4-pole, 3-phase star-connected synchronous motor is considered to be equal and in phase with the terminal voltage under no-load condition. On application of a mechanical load, the induced emf phasor is deflected by an angle of \( 2^\circ \) mechanical with respect to the terminal voltage phasor. If the synchronous reactance is \( 2 \, \Omega \), and stator resistance is negligible, then the motor armature current magnitude, in amperes, during loaded condition is closest to: \[ {(round off to two decimal places).} \]