For the closed-loop system with \(G_p(s) = \frac{14.4}{s(1 + 0.1s)}\) and \(G_c(s) = 1\), the unit-step response shows damped oscillations. The damped natural frequency is \(\underline{\hspace{2cm}}\) rad/s. (Round off to 2 decimal places.)
Open-loop transfer function:
\[ G(s) = \frac{14.4}{s(1 + 0.1s)} \]
Closed-loop characteristic equation:
\[ 1 + G(s) = 0 \]
\[ 1 + \frac{14.4}{s(1 + 0.1s)} = 0 \]
\[ s(1 + 0.1s) + 14.4 = 0 \]
\[ 0.1s^2 + s + 14.4 = 0 \]
Divide throughout by 0.1:
\[ s^2 + 10s + 144 = 0 \]
Compare with standard second-order system:
\[ s^2 + 2\zeta\omega_n s + \omega_n^2 = 0 \]
Matching coefficients:
\[ \omega_n^2 = 144 \;\Rightarrow\; \omega_n = 12 \]
\[ 2\zeta\omega_n = 10 \;\Rightarrow\; \zeta = \frac{10}{24} = 0.4167 \]
Damped natural frequency:
\[ \omega_d = \omega_n \sqrt{1 - \zeta^2} \]
\[ \omega_d = 12 \sqrt{1 - (0.4167)^2} \]
\[ \omega_d = 12 \sqrt{0.8264} = 12 \times 0.908 = 10.90\ \text{rad/s} \]
The value lies within the expected range of 10.80 to 11.00 rad/s.
In the given figure, plant \(G_p(s)=\dfrac{2.2}{(1+0.1s)(1+0.4s)(1+1.2s)}\) and compensator \(G_c(s)=K \left\{ \dfrac{1+T_1 s}{1+T_2 s} \right\}\). The disturbance input is \(D(s)\). The disturbance is a unit step, and the steady-state error must not exceed 0.1 unit. Find the minimum value of \(K\). (Round off to 2 decimal places.)
A continuous time periodic signal \( x(t) \) is given by: \[ x(t) = 1 + 2\cos(2\pi t) + 2\cos(4\pi t) + 2\cos(6\pi t) \] If \( T \) is the period of \( x(t) \), then evaluate: \[ \frac{1}{T} \int_0^T |x(t)|^2 \, dt \quad {(round off to the nearest integer).} \]
The maximum percentage error in the equivalent resistance of two parallel connected resistors of 100 \( \Omega \) and 900 \( \Omega \), with each having a maximum 5% error, is: \[ {(round off to nearest integer value).} \]
Consider a distribution feeder, with \( R/X \) ratio of 5. At the receiving end, a 350 kVA load is connected. The maximum voltage drop will occur from the sending end to the receiving end, when the power factor of the load is: \[ {(round off to three decimal places).} \]
In the circuit with ideal devices, the power MOSFET is operated with a duty cycle of 0.4 in a switching cycle with \( I = 10 \, {A} \) and \( V = 15 \, {V} \). The power delivered by the current source, in W, is: \[ {(round off to the nearest integer).} \] 
The induced emf in a 3.3 kV, 4-pole, 3-phase star-connected synchronous motor is considered to be equal and in phase with the terminal voltage under no-load condition. On application of a mechanical load, the induced emf phasor is deflected by an angle of \( 2^\circ \) mechanical with respect to the terminal voltage phasor. If the synchronous reactance is \( 2 \, \Omega \), and stator resistance is negligible, then the motor armature current magnitude, in amperes, during loaded condition is closest to: \[ {(round off to two decimal places).} \]