Step 1: Formula for maximum power.
The steady-state power per phase is:
\[
P = \frac{EV}{|Z_s|}\sin\delta
\]
Maximum power transfer occurs at \(\delta = 90^\circ\):
\[
P_{max} = \frac{EV}{|Z_s|}
\]
Step 2: Static stability limit.
Given static stability limit:
\[
P_{max} = 2.5 \, \text{p.u.}
\]
Synchronous reactance magnitude:
\[
|Z_s| = \sqrt{(0.1)^2 + (0.3)^2} = \sqrt{0.01 + 0.09} = \sqrt{0.10} = 0.316
\]
Step 3: Solve for \(E\).
Assume terminal voltage \(V = 1 \, \text{p.u.}\):
\[
2.5 = \frac{E(1)}{0.316} \Rightarrow E = 2.5 \times 0.316 = 0.79
\]
Final Answer:
\[
\boxed{0.79}
\]
A continuous time periodic signal \( x(t) \) is given by: \[ x(t) = 1 + 2\cos(2\pi t) + 2\cos(4\pi t) + 2\cos(6\pi t) \] If \( T \) is the period of \( x(t) \), then evaluate: \[ \frac{1}{T} \int_0^T |x(t)|^2 \, dt \quad {(round off to the nearest integer).} \]
The maximum percentage error in the equivalent resistance of two parallel connected resistors of 100 \( \Omega \) and 900 \( \Omega \), with each having a maximum 5% error, is: \[ {(round off to nearest integer value).} \]
Consider a distribution feeder, with \( R/X \) ratio of 5. At the receiving end, a 350 kVA load is connected. The maximum voltage drop will occur from the sending end to the receiving end, when the power factor of the load is: \[ {(round off to three decimal places).} \]
In the circuit with ideal devices, the power MOSFET is operated with a duty cycle of 0.4 in a switching cycle with \( I = 10 \, {A} \) and \( V = 15 \, {V} \). The power delivered by the current source, in W, is: \[ {(round off to the nearest integer).} \] 
The induced emf in a 3.3 kV, 4-pole, 3-phase star-connected synchronous motor is considered to be equal and in phase with the terminal voltage under no-load condition. On application of a mechanical load, the induced emf phasor is deflected by an angle of \( 2^\circ \) mechanical with respect to the terminal voltage phasor. If the synchronous reactance is \( 2 \, \Omega \), and stator resistance is negligible, then the motor armature current magnitude, in amperes, during loaded condition is closest to: \[ {(round off to two decimal places).} \]