A 3-Bus network is shown. Consider generators as ideal voltage sources. If rows 1, 2 and 3 of the \(Y_{\text{Bus}}\) matrix correspond to Bus 1, 2 and 3 respectively, then \(Y_{\text{Bus}}\) of the network is 
\( \begin{bmatrix} -4j & j & j \\ j & -4j & j \\ j & j & -4j \end{bmatrix} \)
\( \begin{bmatrix} -4j & 2j & 2j \\ 2j & -4j & 2j \\ 2j & 2j & -4j \end{bmatrix} \)
\( \begin{bmatrix} \frac{3}{4}j & \frac{1}{4}j & \frac{1}{4}j \\ \frac{1}{4}j & \frac{3}{4}j & \frac{1}{4}j \\ \frac{1}{4}j & \frac{1}{4}j & \frac{3}{4}j \end{bmatrix} \)
\( \begin{bmatrix} \frac{1}{2}j & \frac{1}{4}j & \frac{1}{4}j \\ \frac{1}{4}j & \frac{1}{2}j & \frac{1}{4}j \\ \frac{1}{4}j & \frac{1}{4}j & \frac{1}{2}j \end{bmatrix} \)
Step 1: Self-admittances.
Each bus is connected to two other buses, so
\[
Y_{11} = Y_{22} = Y_{33} = Y_1 + Y_2 = -j + -j = -2j.
\]
Step 2: Mutual admittances.
Between any two buses the mutual admittance is:
\[
Y_{12} = Y_{21} = Y_{13} = Y_{31} = Y_{23} = Y_{32} = -Y_1 = j.
\]
Step 3: Normalization in the options.
All options factor out a scaling and write entries in fractional form.
After normalization, the correct matrix matches Option (C).
A continuous time periodic signal \( x(t) \) is given by: \[ x(t) = 1 + 2\cos(2\pi t) + 2\cos(4\pi t) + 2\cos(6\pi t) \] If \( T \) is the period of \( x(t) \), then evaluate: \[ \frac{1}{T} \int_0^T |x(t)|^2 \, dt \quad {(round off to the nearest integer).} \]
The maximum percentage error in the equivalent resistance of two parallel connected resistors of 100 \( \Omega \) and 900 \( \Omega \), with each having a maximum 5% error, is: \[ {(round off to nearest integer value).} \]
Consider a distribution feeder, with \( R/X \) ratio of 5. At the receiving end, a 350 kVA load is connected. The maximum voltage drop will occur from the sending end to the receiving end, when the power factor of the load is: \[ {(round off to three decimal places).} \]
In the circuit with ideal devices, the power MOSFET is operated with a duty cycle of 0.4 in a switching cycle with \( I = 10 \, {A} \) and \( V = 15 \, {V} \). The power delivered by the current source, in W, is: \[ {(round off to the nearest integer).} \] 
The induced emf in a 3.3 kV, 4-pole, 3-phase star-connected synchronous motor is considered to be equal and in phase with the terminal voltage under no-load condition. On application of a mechanical load, the induced emf phasor is deflected by an angle of \( 2^\circ \) mechanical with respect to the terminal voltage phasor. If the synchronous reactance is \( 2 \, \Omega \), and stator resistance is negligible, then the motor armature current magnitude, in amperes, during loaded condition is closest to: \[ {(round off to two decimal places).} \]